Strengthening of foundation

Status
Not open for further replies.

chella123

Structural
Joined
Mar 29, 2007
Messages
1
I have a situation here where in contractor has poured the footings by draining the water in the pit. However, water table is 3'-0" above the bottom of the footing.

This was not brought to my notice. However, When i formed the core test at 21 days the compressive strength achieved was only 50% of the actual strength. Is there any method to strengthen the footing or should I ask them to demolice and re-do the footing?

Charles
 
Recheck your loads - maybe the footing is OK at 50% - maybe not.

If you are at 3'-0'' below the water table - you have a whole lot of new concerns.

See thread in this forum about three below yours by "sfred11"
 
Concrete placed under water is in the best of cure environments. The placement with tremie or "elephant trunk" chute is a standard proceedure. The results described are possibly due to free fall of plastic concrete onto a muddy subgrade or low quality mix with a shortage of cement. The cores are a good indicator of sub-standard product that needs replacement.
 