I have lots of experience with designing externally bonded CFRP. It is by far the least obtrusive and can be installed in a day. No way new footings, tying rebar, forming, and pumping concrete can be done in any less than a week.
Bond is everything to the design. They NEED to prep the concrete surface properly and clean it of all dust and laitance. They typically just use a grinder with a cup wheel to roughen the surface to at LEAST CSP 3 although I typically specify CSP 4. Good luck getting it though.
I estimate CFRP to be $100 per sq. ft. Per layer. I live in an expensive locale so you may be a bit cheaper but the material is expensive regardless.
You're looking for ACI 440.2R. it's a lot to take in but since you said you have some experience with it maybe you can crank out the design quickly. The equations with all the variables are some of the longest I've ever run across. Once you understand it, it's all strain compatibility based. You will hardly ever reach ultimate strength of the material and will typically be governed by delamination of the material with the concrete. Due to the brittle nature of the failures, there are some pretty conservative strength reduction factors to take. On a side note, some of the manufacturers will even run the design for you free of charge if you use their product but you need to provide them with the demands.
FRP typically comes in 2ft wide strips. I would rip it in 12" wide strips and bond those to the surface and space them out as the design demands it. Run it from top to bottom.
Make sure the Contractor is a certified applicator through the FRP manufacturer. Doesn't mean they are for sure going to be top notch but it's at least a start.
I typically always specify the Fyfe product because I know they have put in the most research, quality control, and customer service. I do not in any way work for them but they are the original and the best in my opinion. I have never used the Simpson product but they certainly gear themselves more to the small time Contractor/DIY crowd. They typically are cheaper. I remember one trade show them trying to sell me on their pre-saturated FRP in a bag! Haha.