Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Stiffness modifier for insulation panel in ETABS 1

Status
Not open for further replies.

ak.t

Structural
Dec 18, 2019
73
Dear All,

If I define the wall as precast sandwich insulation wall panel (max thermal transmittance, U-value of 0.57 W/m2K), what could be the value of stiffness modifier to be specified in ETABS to obtain an actual behavior??

Thank you,
 
Replies continue below

Recommended for you

Not sure what thermal U-values have to do with the price of eggs in China...

In any case, sounds like you're looking to model 'load distribution panels.' CSI Guidance

Few options here:

1) Use null shells, as per link above.

2) Use a thin shell if you need it to be meshed or a membrane if you don't. Make it say 1mm steel plate. Reduce axial membrane stiffness to 1e-5 so it doesn't contribute to lateral stiffness. You couldn't even back calculate what the equivalent steel plate thickness is to account for the weight of the insulation panel (~0.25 kPa = ~3mm steel plate). Reduce bending stiffness in one direction to simulate one-way load distribution.

 
Dear Trenno,

It is a load bearing precast concrete walls that consist of two concrete layers joined by stainless steel connectors with an insulating layer between them. The insulation layer is continuous over the entire surface area.

insulation_panel_xjelii.png
 
AkshikaS,

For the cross-section that you have added, the stiffness modifiers should resemble the way the structure behaves.

Modifiers I would be thinking something like:

Membrane, mass & weight modifiers no more than 0.75 of modifier that would be applied for a 200thk wall (150mm / 200mm).
Bending modifiers even further as you have two thin panels instead of 1 insitu panel. 0.1 of modifier that would be applied for a 200thk wall. (65^3+85^3)/200^3.
 
Dear rscassar,
Why do we calculate like this (65^3+85^3)/200^3.? Could you please explain me?. Thank you.
 
Cause the bending stiffness is calculated depth^3. Cause you have create a 65mm panel and an 85mm panel without any coupling between the two of them, the stiffness is calculated each panel individually.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor