Steel Vierendeel Truss End Connections
CUChalk
3
I am working on designing a steel-framed Vierendeel Truss using HSS verticals and wide flange chords. The reason for this is so it can effectively be hidden inside of an 8" CMU wall. There's more to the backstory of how we got to this point, but it's not relevant to my question.
I have used RISA to size members and ensure deflections meet L/600 criteria. I have designed the moment connections for all the vertical branches to the chords using Blodgett's welded structures book and Alex T weld group spreadsheets. The final concern is how to connect this truss to the face of an HSS column that is already in place. I can't sit it on top of the column because the column extends up to a roof and this truss is at the second floor level. In my RISA model, I've used a pinned support on one end and a roller support on the other end. My question is if I have a vertical branch right at the end of the truss with significant moments at the connection points (~50 ft-kips), is it even possible to do just a shear connection or does it have to be a moment connection? Granted, even if I could theoretically do a shear tab bolted to the chord, I'm not sure you can physically do it because I need stiffener plates for the chords at each vertical-chord connection (see Revit screenshot). I have looked at pulling the end verticals back a foot from the bearing points to make room for a standard shear tab type connection (RISA screenshot).
I've never done a Vierendeel Truss so I'm just curious what a typical end connection would be in a situation like this or am I doing something unprecedented here? Any thoughts are appreciated.
Thanks in advance,
CUChalk
First - that's a massive looking truss tying into a skinny little column.
My old mentors always taught me "if it doesn't look right it probably isn't."
Second - I would first try to push the last 10x4 vertical back just a bit but connect all the shear through a single plate tab bolted to the top chord - assuming the top chord has enough depth to accommodate the needed bolts. If not then some custom alteration at the top chord end to create room for the bolts (i.e. cut back its bottom flange and extend the web down for more bolts).
Just feels wrong to bear this truss off its bottom chord. I can't say why but would just refer to the quote above.
It's certainly not an ideal situation. These columns are already installed though, as is the SOG, so adding a beefier post next to this one would result in slab demo, some CMU demo and footing modifications. What happened was a long storefront was added to a CMU wall late in the game, we didn't catch it, and unfortunately that wall is carrying second floor joists. My initial thought was to just size a beam to carry the CMU that would sit just above the storefront like a typical lintel and then size another beam at the floor level to carry the joists. The problem is getting a 30' long beam carrying floor loads to fit within an 8" CMU wall. Not to mention that the upper beam would essentially just sit on the CMU infill, putting all the load on the lower beam anyways. Our thought was to tie the 2 beams together and get some kind of truss action out of them so they would move together, and thus the vierendeel truss idea was born. This is also at the main entrance of the building and there's no ceiling to hide anything so I'm stuck between a rock and hard place.
Also your model has slip at one end and I would be looking to detail it that way or investigate the consequences of locking it in.
I like the idea of a simple shear tab on the top chord and potentially another shear tab at the bottom chord perhaps with slotted holes.
I'd also be looking at a stiffened seat connection with possibly an out-of-plane plate restraint at the tope. A seat lets you easily avoid the issues of localised load on the HSS face.
I'd also be very careful about the effects of eccentric load on the column here.