Typically, I size studs assuming a 'pin' condition at the bottom track.
If the studs runsfull height of say a 1-story building, You have a 'pin-pin' condition. And the size of the stud is determined accordinly.
A hinge condition is created under long windows, for instance, when the track at the bottom of the stud is fastened to the foundation in the same way (a 'pin' condition) but a window interupts the stud. Then you have a 'pin-free' condition for this stud. If the wind blows on the window, which translates the lateral load to the top of the interupted stud, then there is no mechanism to handle the lateral load.
Been involved in a couple of retrofit jobs over the years to stiffen these kind of conditions after the wall/window began deflecting horizontally too much.
On one story buildings, with non-load bearing exterior stud wall, it is common to run the stud up past the roof steel line some distance to form a parapet. The top of the stud is braced laterally to the roof framing. A vertical slip connection is required between the stud and roof framing to allow the roof framing members to deflect under load, without imparting that vertical load to the studs.
Most of the stud supplier's have standard connection clips for this situation, as it is a very common thing.
Hopefully this makes sense.