Upjengnr04:
Actually, the OSHA 5000lb. criteria is an ultimate strength criteria (it can fail at 5001lbs.), their requirement for an attachment point/fixture, for an unknown loading, direction of loading, type of load, etc.etc. If the loading is controlled and understood, and designed for by a registered engineer, you can get by with a lesser loading. Energy absorbing lanyards, distance of fall, etc. can be taken into account in the analysis, and made part of the system. I believe they do require a 250 or 300lb. man with 50lbs. of added equipment. You just have to dig through the OSHA requirements to dig this stuff out, and that’s not an easy matter either. Talk with your local OSHA office, they are instructed to be helpful, when you come to them with a reasonable question, during the design phase, and before the accident. Then, also, the local office interpretation is what you have to deal with first during an inspection or if anything does go wrong.
It’s a crazy thing these days that we don’t want to do anything (can’t do anything) which is not explicitly covered by a paragraph in a code or std. You say... “ I decided to use common sense and basic engineering to back up my opinion.” Can a falling guy really exert 5000lbs. of loading on an attachment point, only 16g, or is the 5000lb. requirement intended to make non-engineered attachments and fixtures unwise or difficult to do? There are a thousand questions unanswered in your OP...: is the guy working above or below the jst., length of fall? Is his attachment point to the top chord or bot. chord? Are these attachment points at a panel points on the jsts., or otherwise? As part of this system can they apply some temporary bracing or load distribution to several other jsts.? Is this system for erection of the jsts. or being used on a completed roof system? I’m not saying it is a simple half page calc. problem, but you are trying to help your client, aren’t you? And, certainly he should willing to pay you for your effort in helping him.