Depends on what you mean... are you looking for ways to eliminate the fabricator from actually coping the beam or ways to eliminate the typical failure modes associated with them?
Your solution of of an extended shear tab would take care of both (provided the extended tab works for buckling as well). There are also some major advantages to erecting beams since they can be dropped in straight instead of "swung" in (not sure if that's even a word). Cost would vary from fabricator to fabricator but in general these extended tabs would likely cost more if they needed to be welded to the top or both flanges.
As far as strengthening a coped beam, you can:
1. Weld a plate to the top of the coped web to create a false flange.
2. Weld a "doubler" plate flat on the web the extends past the cope to effectively thicken the web section prone to buckle.
3. You could use clip angles with longer in-standing legs that extend up to or past the cope that achieves a similar effect to #2.
I'm sure there are other ways but these are all options I've used in the past.