Steel Beam to Wood Post Connection
SE2607
297
Does anyone see any issues with this detail?
TIA
Pretty sure you're saying a W10x15 is 8 1/8" tall, and I like steel to create torsional stability in the beam (usually an end plate).
Oops. My bad. It's a W8x15.
I can put a pair of stiffeners near the end of the beam., but won't the nailer attached to the floor sheathing provide torsional resistance?
Thank you for your response.
I question the ability of the 2 or 3 10dx1-1/2" nails near the end of the beam to meet the requirements of AISC J10.7. But you have the whole picture - if you can conclude that it does the job, then great.
Normally, I bear the steel beam directly on the PSL post, but I see no issue with your detail, especially considering the relatively light load of only 4k. Rather than use a pair of stiffeners, I'd have a 1/4" plate welded to the end of the beam.
The end plate is cheap. I would specify it regardless.
I would also prefer to connect directly to the post, but I agree for light loads it probably doesn't make much difference.
For me, I would have no attachment to the post and use studs instead of PSL for only 4K. The floor diaphragm will keep it in place.
No attachment?
How would you comply with the "positive connection" requirement of the code? Perhaps that's only a requirement in the IBC and not the IRC. The Northridge earthquake, not a design level EQ, generated vertical accelerations of greater than 1g.
To be fair, I doubt anything is surviving a 1g acceleration.
If the engineers designing don't do their jobs, perhaps....
Where XR practices, seismic loads will be of very minimal concern.
Where is that, exactly? I've always done it because it makes sense to do it, but nobody has ever been able to point me to a specific place in the code where such a requirement resides, and I've never stumbled across it.
I realized that when I wrote the post, but I did it (wrote the post) anyway.
It's there because I've had a plan check comment. While addressing the comment, I checked the code reference to verify, but I don't recall where it is.
To me, a couple of A34s is not asking for much.
That's why there was so much damage for an EQ much less than a design level EQ. Northridge is a thrust fault causing predominantly vertical acceleration whereas most of the faults in California are strike slip faults, which are predominantly horizontal.
For vertical accelerations of 1g? Lateral sure.
I don't design for 1g vertical. The code requires Ev = 0.2 * 0.7 * SDS, allowable stress design.
A random spot in downtown Los Angeles has a SDS =1.55, so the vertical force would be about .22g.
You will get a hump over the steel beam when the joists shrink...not a structural problem, but very noticeable.
Agreed. I was just curious if you remembered the code. Would come in handy when I tell people to attach things that they haven't had to attach before...
Honestly, in my area, I have seen a flush residential steel beam fastened to wood support maybe 2 times in the last 30 years.
The next time I find it, I will post here.
So, what other methods have you seen?
Not sure about @XR250 , but I have seen shallow steel flush beams in residential construction just sitting/bearing on the wall top plate just like a typical floor joist. For deeper beams or drop/soffit beams I have seen them bearing directly on a stud pack that is shorter than the typical wall studs with a tall "king" stud on each side of the beam to box it in.
