I have a 3" 50# condensate return line that has about a 10 ft vertical drop and a 2" reduction, a 90 over to a 2" Y-strainer and a steam trap all along a 3' section of horizontal pipe in the middle, and a 90 back up.
The problem here is that the steam trap keeps eroding away, along with the pipe on the horizontal run (vertical runs are always OK). The pipe is schedule 80 carbon steel and was paper thin the entire ID after about 1 year of service. It is an ongoing problem every year. Most recently the pipe upstream of the trap failed at the threads and the Y-strainer at the 10:00 position. The steam trap has been ultrasonic tested and is working properly.
We brought the vendors in and they seem to think it is chemical attack from aggressive condensate. I have a hard time believing that (see chemical composition below) so I wanted to listen to your ideas. It seems like an erosion issue even though the fluid velocity is low (Assuming 100% condensate). Possibly something to do with 2 phase flow?
Process conditions are 50# condensate
10-17 kpph flow (2-4 ft/s)
<25 ppb O2
pH 9.0
conductivity 9.6 mmhos
Iron 0.09 ppm
Total Hardness 0.0
Here's a link to the trap
-Mike
The problem here is that the steam trap keeps eroding away, along with the pipe on the horizontal run (vertical runs are always OK). The pipe is schedule 80 carbon steel and was paper thin the entire ID after about 1 year of service. It is an ongoing problem every year. Most recently the pipe upstream of the trap failed at the threads and the Y-strainer at the 10:00 position. The steam trap has been ultrasonic tested and is working properly.
We brought the vendors in and they seem to think it is chemical attack from aggressive condensate. I have a hard time believing that (see chemical composition below) so I wanted to listen to your ideas. It seems like an erosion issue even though the fluid velocity is low (Assuming 100% condensate). Possibly something to do with 2 phase flow?
Process conditions are 50# condensate
10-17 kpph flow (2-4 ft/s)
<25 ppb O2
pH 9.0
conductivity 9.6 mmhos
Iron 0.09 ppm
Total Hardness 0.0
Here's a link to the trap
-Mike