Retaining control is a matter of the valve opening rather than simply the dP. If the valve gets too far open or too far closed, you lose the ability to control the process be it pressure, flow, whatever. Granted, high dP leads to high outlet velocities and that can create other issues (noise, vibration) but those aren't directly 'control' issues (or not as I consider them).
Generally, for sizing, you don't like to go much under 20% or over 70% open on the control valve. In operation, I tend to push that to 10% to 80% or 85%.