Ok, since this issue can be situational, here's our situation:
This air handler serves only one zone, the sanctuary of a large church with a very expensive organ. The humidifers (and most of the controls configuration) exist to keep that organ close to 50% RH. People come second, but we try to make them comfortable, also. Some of those people are on a stage under 30+ spotlights. This means we have to have the moist air as cool as possible to deliver to the stage area and keep them from dissolving into puddles of sweat. Much of the seating area ends up being tempered back with electric reheats. The humidifiers typically only run from October to March when the outside humidity drops. The rest of the time, we regulate (primarily) the chill water temperature setpoint to control humidity, as well as chill water flow rate. We are able to use outside air very little, as it rarely has the right combination of temperature and humidity to be of much use. Cold air needs to almost completely saturated to end up at 50%RH when heated to 70 degrees F.
Most of the time, this zone is unoccupied or lightly occupied and we can let the temperature vary as long as the sub-zone that surrounds the organ (partially enclosed) remains within a fairly tight temp range (very tight during organ usage). This sub-zone has electric heat (reheats).
But during occupancy, even if it is quite cold outside, we'll be running the cooling coil 100% and the humidifier 100% and they will be canceling each other out in terms of both temp and humidity, to some degree. Fortunately, lots of people add a little humidity, instead of just needing to be cooled down (which reduces humidity).
The humidifier unit is installed directly upstream from the coil (26" of separation), so there is little chance for the steam to mix in with the airstream before the coil condensates most of the moisture back out.
The unit has two electric heat sections, but they are virtually never used. The steam provides more than enough heat at those rare times when they would normally have some benefit.
We do have a fair amount of mold on the supply fan cages in the exit end of the air handler, but not much more than the other air handlers that have no humidifiers.
There are times when we have to abandon humidity control for a brief period of time (when the sanctuary is full and everyone has a lit candle, eg.) and do a 100% outside air exchange. 42 degree F water through the coil just isn't enough. Getting too dry won't damage the organ's components if it doesn't last very long. Temperature is critical during performance, it affects tuning.
===
So, if removing excess liquid moisture is the purpose of putting the coil downstream from the humidifier, they should have put the humidifier farther upstream, to give the air more time to integrate the steam. And if we ran the coil just cold enough to remove excess water, we wouldn't get enough cooling during occupancy.
But, if they *had* put the coil upstream of the humidifier, then we *might* have a bigger moisture problem in the exit end of the handler and those ducts... Running the humidifiers at 100% with the coil manually shut off, might tell us if there would be a moisture problem....
Hmmm....