Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JStephen on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

stationary engine mounting info needed

Status
Not open for further replies.

brutus1955

Mechanical
Joined
Aug 19, 2003
Messages
57
Location
US
i have been researching the answer to how i can
decide on the dimensions of a concrete base for a single cylinder diesel engine.

is there anyone on here that can lead me in the right direction or help me to find source information.

thanks
bob g
 
Your engine manufacturer should be able to provide you some guidance.
 
Consider looking at Slidruleera site at:

or


I have see foundations sized using concrete mass of 4 times the machinery with rebar is installed where it will improve the structural capacity of the foundation, two layer approach of top and bottom. Some codes specify allowable vibration limits (like NEMA MG-1 allows 0.15 ips while resiliently mounted and 0.12 while rigidly mounted).
 
the engine manufacture does not provide support for this engine, long out of production

Boo:
thanks for the links they are exactly what i was looking for

bob g
 
Both of BOO1's fine links mention the height of the CG is important, with a relatively tall or deep foundation having a rocking frequency much lower than the simple vertical calculated frequency. Thus relying heavily on one of the ratio-of-masses in design leaves me vulnerable. Correcting foundation resonance problems is generally BIG trouble.
 
Tmoose's comment is a valid point. A few other rough rules of thumb:

Foundation depth >= 1/5 width
Foundation depth >= 1/10 length
Top of Foundation to CG of Machine >= 2/3 to 1 x Foundation Width
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top