Suggestion: A distinction is supposed to be made among:
1. Motor starting current, namely:
The current drawn by the motor during the starting period (a function of speed or slip).
2. Motor locked rotor current, namely:
Steady-state current taken from the line with the rotor locked and with rated voltage (and rated frequency in the case of alternating-current motors) applied to the motor.
3. Motor inrush current, namely:
The rapid change of current with respect to time upon motor energization. Inrush current is dependent upon the voltage impressed across the motor terminals and the motor inductance by the relationship V=L*di/dt.
The original posting refers to the starting current as defined in item 1.
The starting current includes inrush current and if the motor happens to stall, the motor locked-rotor current, as defined in item 2, materializes.
If the discharge valve is used properly, there will be two modes of operation of the motor with one motor starting current, namely:
1. The motor starts with relatively low shaft load when the discharge valve is closed. This implies that the motor starting current will be converging faster to the motor steady state current that is lower than the motor running load current (usually designed lower than the motor rated current).
See Reference: IEEE Std 399-1997 Chapter 9 "Motor Starting Studies"
for motor starting time calculations and equations, e.g. Equation 9-18.
2. Discharge valve becomes opened. The motor is loaded as designed by the motor-pump set integrator.
The motor experiences the second part of its motor starting current in terms of its adjustment or increase to its designed motor current value. There may be a motor current transient depending how fast the discharge valve is open. This current increase is not normally referred to as an inrush current even if it may have some parts of inrush current resemblance.
To summarize the advantage. The motor starts faster with the same inrush current, however, the current levels off at lower than the designed current. When discharge valve opens, the motor current adjusts to its running current as designed by the motor-pump set integrator.
Advantage of this concept is in the smaller size of the motor that accomplishes the same function as the larger size of the motor that may be required for the discharge valve kept in open position, and in the starting current that converges to the lower steady state current initially when the motor shaft load is lower.