Returning to the original posting, I wonder whether we have adequately answered the question.
The original question was in regard to the effect of the discharge valve on the starting current of the motor.
Firstly, the closed discharge valve will reduce the shaft torque presented by the pump during start.
If you use a full voltage starting method, the reduction in starting torque will serve to reduce the starting time, but will not alter the start current. Under full voltage starting conditions, the start current is a function of the motor design, the applied voltage and the rotor speed.
The start current will initially be the Locked rotor current and will reduce gradually as the motor accelerates and will only fall quickly as the motor reaches full speed.
At the instance of the contactor closure, there is an inrush current that will last for a couple of cycles only.
The locked rotor current of the motor is typically in the range of 550% to 900% of the rated current of the motor. The inrush current could be as high as twice this.
Secondly, if you use a reduced voltage starting method, then the lowest start current is dependent on the motor design and the shaft load. By reducing the starting torque required by the pump, you will reduce the minimum start current required to start the pump. This can only be achieved provided that an appropriately engineered starting system is employed.
To summarise, the statement "limit starting current on the motor" could be true if an appropriately engineered reduced voltage starter is used, otherwise, the start current will be the same, but for a shorter period of time.
Best regards,
Mark Empson