Suggestion to DanThomas (Electrical) Jan 19, 2004 marked ///\\Thanks again for all the replies. One of the links that Jraef posted (
is exactly the circuit used in the compressor we have. If you look at the schematic, you'll see that there is no overload protecion for leads T4, T5, or T6. In my case, one of the contacts failed (T5), which put the motor in a "single phase" condition.
///Please, what was the upstream motor starter protection?
There are many applications where a motor is sensitively protected by an inverse time circuit breaker (NEC permits up to 150% of the three phase wound rotor induction motor full load amps. In very old times, there was nothing better.\\The overload relay trips out at around 64 amps (line current). However, in a delta circuit, the phase current is .58 times the line current. This means that at full load the "phase current" is approximately 37 amps per phase.
Although this configuration has been employed for many years, I believe that it is only effective for an overload condition, and nothing else. As in my case, the existing overloads did nothing to protect the motor when one of the delta contacts failed.
That is why I asked if putting one overload relay in each delta winding (rated at 38 amps) would offer more protection against single phase conditions. The main overload (rated at 64 amps) would protect the motor against overloads.
I called Ingersoll-Rand and they said that they see this happen all the time, and that he overload usually only works if there is an overload (compressor starts to bind).
///The compressor starts in the most adverse motor shaft load condition.\\Does this make things any clearer?
///Definitely it does. Especially, if the motor line protection is not by a sensitive three pole inverse time circuit breaker. Incidentally, this has not been addressed yet.\\ Thanks again for all the input. Dan Thomas