Pocko
Electrical
- Mar 5, 2003
- 8
Hello,
I hope things are well in your part of the world; just a long winded post to verify a few things...
We have two mill motors (on a multishaft disperser) currently being started in a star/delta arrangement. The production bosses want to put a larger diameter "blade" on the end of each shaft (going from 10" to 12")in order to get quicker grind times. They vaguely tell me this been tried once in the past and the motor's kept tripping out on overload, so they reverted. I've been asked to look over the situation.
Each is a 45kW 3Ø motor with a F.L.C rating of 80.9A, 415v, S.F 1.15, 1445rpm.
The overload is situated correctly in the circuit (bottom of the Line contactor), and is currently set to it's max. range of 40A. It seems to be a single range overload.
The cores to the star/delta windings are rated at around 40A/Ø odd under our code.
My query is in regard to the overload setting, by my calc's (80.9 x 0.58) 46.922A should be the correct setting for this overload. So i believe they can not get the full work out of these motors because of the overload's range limitatons.
I can't really allow the extra 15% to the total in this case because the motor's located in a hazadous area, but that extra 7 amps may be enough to tip the scales in our favour. I don't know if the last sparky tried to upsize the overload to 48A for his trial, but i assume he didn't. I'd like to see the cable's upsized too.
I'm going to tong the supply to the line contactor tomorrow during a batch if i get time, to see how hard they are working it at the moment.
If we upsized the overload, and threw the bigger blade on only to find the motor was overloading, this would be a nasty situation for us as it would be a BIG job to empty this vessel with raw product in it (when a batch starts run time is usually around 8 hours). Success would equal batch times of around 4-5 hours and would make many people happy!
Do you think this modification is viable? I'll post any extra information i find out.
Thank you for your time and any thoughts on the situation would be welcomed, Regards - Chris.
I hope things are well in your part of the world; just a long winded post to verify a few things...
We have two mill motors (on a multishaft disperser) currently being started in a star/delta arrangement. The production bosses want to put a larger diameter "blade" on the end of each shaft (going from 10" to 12")in order to get quicker grind times. They vaguely tell me this been tried once in the past and the motor's kept tripping out on overload, so they reverted. I've been asked to look over the situation.
Each is a 45kW 3Ø motor with a F.L.C rating of 80.9A, 415v, S.F 1.15, 1445rpm.
The overload is situated correctly in the circuit (bottom of the Line contactor), and is currently set to it's max. range of 40A. It seems to be a single range overload.
The cores to the star/delta windings are rated at around 40A/Ø odd under our code.
My query is in regard to the overload setting, by my calc's (80.9 x 0.58) 46.922A should be the correct setting for this overload. So i believe they can not get the full work out of these motors because of the overload's range limitatons.
I can't really allow the extra 15% to the total in this case because the motor's located in a hazadous area, but that extra 7 amps may be enough to tip the scales in our favour. I don't know if the last sparky tried to upsize the overload to 48A for his trial, but i assume he didn't. I'd like to see the cable's upsized too.
I'm going to tong the supply to the line contactor tomorrow during a batch if i get time, to see how hard they are working it at the moment.
If we upsized the overload, and threw the bigger blade on only to find the motor was overloading, this would be a nasty situation for us as it would be a BIG job to empty this vessel with raw product in it (when a batch starts run time is usually around 8 hours). Success would equal batch times of around 4-5 hours and would make many people happy!
Do you think this modification is viable? I'll post any extra information i find out.
Thank you for your time and any thoughts on the situation would be welcomed, Regards - Chris.