I am running a new STAAD simple truss model. The original design truss drawings indicate the top chords to be double angles, 8x8x5/8 with 3/8 gap. The original plans show a compressive load of 326 kips. The truss is a HOE type. The top chord panels are at 7.0 feet on center.
The new design actually sheds some of the truss load. STAAD gives a compressive load of about 305 kips for same top chord member. In the code check, it says that the chord is over stressed!
From quick kl/r calculations, rx will govern, for A36 steel I came up with allowable axial load of 377 kips for 7.0 unbraced length. AISC tables give 371 kips which is very close to my hand calculations.
Does anyone know why STAAD is failing the top chord members? Are there any particular parameters commands that I need to add to STAAD?
Regards,
Lutfi
The new design actually sheds some of the truss load. STAAD gives a compressive load of about 305 kips for same top chord member. In the code check, it says that the chord is over stressed!
From quick kl/r calculations, rx will govern, for A36 steel I came up with allowable axial load of 377 kips for 7.0 unbraced length. AISC tables give 371 kips which is very close to my hand calculations.
Does anyone know why STAAD is failing the top chord members? Are there any particular parameters commands that I need to add to STAAD?