For the loop test of rotor:
The shaft need not have a hole in it, could also be a spider type.
If not spider and no hollow shaft, there is no option for rotor loop test, but you could clamp onto the rotor at each end to directly apply voltage, rather than induce it.
The intent in both cases is to create current in the bars... if there is a bar/joint with high resistance connection, it should show a hot spot on thermography or flux anomaly with green paper.
In both cases, there are lots of variables that can influence the flux and current beside broken rotor bars. Not a great test imo but I like the clamp test better than the loop test.
Here is an article by EASA which is a survey of methods for checking rotor bars
Neither method is mentioned in there but they are mentioned in motor repair specs such as EPRI's medium voltage repair spec.
Attached are results of thermography during clamp test of an 800hp from our plant that showed rotor defect based on running current signature analsysis (45 db down). The infrared shows hot spots at same locations as visible cracks. After resoldering, the current signature analysis restults returned to normal (60db down).
Some rambling discussion of this particular case and the monitoring methods in general here:
=====================================