Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Square Footings combined with Stemwall Foundations: A rational approach 1

Status
Not open for further replies.

medeek

Structural
Mar 16, 2013
1,104
Occasionally I encounter a point load from posts that exceed the bearing capacity of a stemwall foundation footing. I then typically call out a square footing (ie. 24"x24"x12" w/ (3) #4 bars each way) to increase the bearing capacity at this location. However, in certain situations I've noticed that the number don't quite work for the stemwall footing alone or the square footing alone. It would seem logical that one could combine the bearing areas of both the continuous footing and the square footing and the total bearing area would account for this overlap as shown in the diagram below:

COMBO_FTG1.jpg


Does this seem like a rational and reasonable assumption to make?

Up until now I have simply ignored the contribution from the stemwall footing and sized the square footing as if it were an isolated footing.

A confused student is a good student.
Nathaniel P. Wilkerson, PE
 
Replies continue below

Recommended for you

I don't see it. I see 1V:0.75H = 2V:1.5H.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor