Let me start by saying that I'm not a P.E., however, I've spent years in substation construction, maintenance, and operation so the subject of lightning is one that concerns me almost daily. Although I'm sure there are many devices and practices that people will recommend throughout the world, there is only one "fix" that I truly believe is a big help and is as close to a "true" remedy for dispersion of energy from a lightning strike as you can get. That remedy would be properly sized and carefully installed grounding. Whether your transmission structures are steel or wood, a properly sized static or sheild wire that is connected to earth at every structure with a large enough copper conductor is the answer. Of course, once that copper conductor gets to earth level, there is work to do there as well. If you know you are in a lightning prone area, provide adequate earth contact by properly installing ground rod(s) (more than one in your case would probably be a very good idea) and making sure they are connected with connections that are specifically rated for direct earth bury service. To me, mechanical connectors are not to be used in this instance. It amazes me yet today that there are companies with lightning prone lines(and substations for that matter) who haven't yet discovered exothermic welds for making grounding connections! At my current place of employ, grounding practice has changed recently. Transmission line and substation structures are now solidly grounded using large(1/0 to 4/0) copper conductors. Ground rods are installed liberally and spaced several feet apart and are connected using exothermic welds. The results speak for themselves. Few if any flashovers to 13KV underbuild conductors have occured and the breaker operations during storms (in my estimation) have been cut by at least 75%. On wood pole structures, #4 solid copper wire is the MINIMUM conductor size(many times #2 awg and 1/0 is used) and in addition to a butt rap at the bottom of the pole, at least 1 ground rod (5/8 in. X 10ft.) is installed 4 to 6 ft. away from the installed pole butt into undisturbed earth. When grounding steel towers or any steel fixture that is subject to lighning strikes, carry the grounding conductor all the way to the top of that structure and attach directly to your shield wire. Don't allow "coils" or "pigtails" to be installed in the slack area near the shield conductor in these conductors either. Keep them as straight as possible and keep bends in the grounding conductor gentle and sweeping. Sharp or abrupt bends or kinks should not be tolerated. This "new practice" may ruffle the feathers of some linemen, but when they witness the results, the complaining should stop. Don't rely on the steel structure itself to carry the energy of a strike. Bonding the base of the steel using a 5/8in. X8ft. ground rod and a short piece of #6 copper is NOT proper grounding.(At least here in the middle of the U.S.) Now, grounding is not cheap by any person's estimate, but it sounds like you've had enough damage and destruction to warrant some expenditure on problem prevention. It has been my experience that grounding is without a doubt the most misunderstood subject at many utilities today. It seems the folks who make the decisions are always looking to cut expenses somewhere,(aren't we all?)but cutting the grounding is probably the LAST place where cost cutting should take place. I'd forget the splined balls and get some large copper conductor and some 3/4in. X 10ft. ground rods.