Eng-Tips is the largest forum for Engineering Professionals on the Internet.

Members share and learn making Eng-Tips Forums the best source of engineering information on the Internet!

  • Congratulations dmapguru on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Spinning class cooling load

Status
Not open for further replies.

emalsyd

Mechanical
Joined
May 10, 2006
Messages
43
Location
US
A local YMCA wants to add cooling to 14' x 28' room they use for spin class. There are 15 bikes in the room. What would be the heat load from each person cycling. I'm using Trane Load 700 to calculate how much cooling they will need but I'm not sure what the load of the spinners would be?
 
I'd guess around 1500 BTU/hr, 1/3 sensible, 2/3 latent.

ASHRAE handbook should have a table of suggested values, including a line for exercise.
 
If we go with IRstuff's 691W figure I would imagine that must include both external work done and "waste" heat from the body.

If you already have a heat gain number from the bike manufacturer make sure that you're not double counting.
 
depends on how fit the people using the spinners are! lol
 
710 btu/h/person Sensible
1090 btu/h/person Latent is what HAP says for athletics.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top