Chiller cooling loop for multiple cosmetics mixing machines - need advice
HollyBoni
We make various cosmetics products at our company, and we're looking at getting a chiller to cool our jacketed mixing machines. I already built the "hot" side of the loop for 1 mixing machine with a circulation pump, expansion tank, plate heat exchanger. Now i'm looking at building the chilled water side.
I'll have a chiller, pump, buffer tank. We're planning to have 3 mixing machines that need cooling. Each mixing machine will have it's own heat exchanger, PID controller, and circulation pump on the hot side. The PID controller of the mixing machines controls the heating elements inside the mixing machine, and when cooling is needed, it opens some kind of a valve (I built the first mixing machine with a motorized ball valve).
When a mixing machine needs cooling, the PID opens a valve, which let's chilled water flow through the heat exchanger of the mixing machine. We might cool 3 mixing machines at the same time, or we might only cool one at a time. The chiller might also run without any of the mixing machines calling for cooling. Each mixing machine needs a fixed water flow rate regardless of how many mixing machines are being cooled at the same time.
So my question is, how should I build out this system, what's the common setup for something like this?
My idea so far:
I'll have 1 pump that circulates water between the chiller and the buffer tank, and nothing else. Then a secondary pump that circulates water between the buffer tank and the mixing machines. This is where I kind of get lost.
Should I get one bigger, smart pump that can regulate itself based on stuff like differential pressure, and then just have zone valves that the PIDs open? Or should each zone get it's own smaller pump instead? Should I do a bypass line and branch off of that? Should I get a more powerful, "dumb" centrifugal pump and use things like PICV valves to regulate flow to the mixing machines?
The solution is probably pretty simple and i'm just overthinking it. Any help would be appreciated.
Like you said, there are a few ways to do it.
If you want to keep the primary-secondary idea where you are using one pump for the chiller and another for your mixers (and you're willing to replace some valves), then you could use 3-way valves at each mixing machine that will bypass the flow when it's not needed or allow the flow through when it is. Two mixers would branch off of a main supply and return line, and the last mixer would be what connects the supply to the return. Use a variable speed motor on the secondary pump and some balancing valves for each mixer and you'd be set as far as I can tell.
Disclaimer: I've only designed one chilled water system and the rest of the systems I've looked at have been conceptual.
You only need capacity control on one side of each heat exchanger. You don't need flow control or variable speed pumps as long as you use 3-way valves.
If the mixer side has a valve that can control cooling water temperature, then just let the chiller side flow. The chiller will maintain its setpoint temperature, and the buffer tank will absorb thermal mass to prevent the chiller from short-cycling. Chillers like to have stable flow and temperature, they really don't like having flow turned off. Pull from the buffer tank to keep the chiller stable, then through the chiller, and then to the heat exchangers.
Three small mixer loops, one large chiller loop with the 3 heat exchangers in parallel. 4 fixed speed pumps that run full time, and 3 3-way actuated control valves total. You may need balancing/throttling valves depending on how the system arrangement and pump sizing goes on the chiller side.
You can get fancy and add more features, but its more complications and more inter-dependency and more complicated controls.