Section 9.3.4.1.2 appears to be the same in the two versions (13 and 16). The provision quoted above as 6.1.7.1.3 can be found in 9.3.3.3.2.3 in TMS 402-13.
I recently heard a comment in some continuing ed. concerning this topic and it was the presenter's opinion that the requirements of 7.3.2.6 (b) force the use of standard reinforcement in lieu of jt. reinf. for SRMSW. Specifically the term "shall be embedded in grout"
(b)The maximum spacing of horizontal reinforcement required to resist in-plane shear shall be uniformly distributed, shall be the smaller of one-third the length of the shear wall and one-third the height of the shear wall, and shall be embedded in grout. The maximum spacing of horizontal reinforcement shall not exceed 48 in. for masonry laid in running bond and 24 in. for masonry not laid in running bond.
The presenter was very knowledgeable in masonry design and the code committees and quite possibly a frequenter of these forums..
I questioned this interpretation upon returning to the office based on the following:
-Section 9.3 of TMS 402 gives guidance for use of joint. reinf. used as shear reinf in SDC D, E, and F (although I cannot find a similar provision for ASD design in 8.3). Why would there be provisions for jt. reinf. in shear walls in high seismic design categories if it were not allowed for SRMSW??
-Even if it is the intention to limit reinforcement required to resist in-plane shear to standard bars in bond beams, I do not feel like the provision quoted above (9.3.2.6) would apply for reinforcement used solely to meet the minimum horizontal reinforcement requirements (since it specifically says "required to resist in-plane shear").