From the special inspection form in my jurisdiction, California Building Code (CBC)
Table 1705.8 – Cast-In-Place Deep Foundation Elements
For concrete elements, perform tests and additional special inspections in accordance
with Section 1705.3. (requires verifying mix design, rebar placement, concrete slump, make concrete cylinders for strength tests, inspect form work - would all be required for a cast in place deep foundations)
1705.3 Exception: Special inspections and tests shall not be required for:
2) Continuous concrete footings supporting walls of buildings three stories or less above grade plane that are fully supported on earth or rock where:
2.1) The footings support walls of light-frame construction.
2.2) The footings are designed in accordance with Table 1809.7.
2.3) The structural design of the footing is based on a specified compressive strength, f 'c, not more than 2,500 pounds per square inch (psi) (17.2 MPa), regardless of the compressive strength specified in the approved construction documents or used in the footing construction.
1809.7 Prescriptive Footings for Light-Frame Construction i.e. shallow foundations.
Now I normally have not been required to do special inspections per 1705.3. The structure is light frame, the concrete is 2500 psi. However it is supported on grade beams, not prescriptive shallow foundations. I discussed this with the building official and he also said they do not normally require this. His logic was that the grade beams and cast in place drilled shafts far exceed prescriptive footings for light-frame construction per 1809.7. Can anyone confirm this is the correct interpretation? We are also assuming that the requirement of exception 2 are all AND clauses, that it must meet 2.1, 2.2, AND 2.3. Do all deep foundations require performing tests and special inspections in accordance with CBC 1705.3