Thanks for the replies. Yes, I have seen and have read that Operating Instructions manual. To address the need for isolated relay contacts in parallel configurations (two of these sharing the same source), my intention is to use the relay outputs of a 1766-L32BXB PLC. The PLC has 6 onboard relay outputs rated for up to 15A at 120V AC. The pumps will be controlled via 4-20mA signals from the PLC logic, based on various discrete inputs from external components (sensors, switches, etc). In past projects I've worked on we used overload relays just before some mechanical contactors to protect the motors. This gamma/L is a different type of pump and is much smaller though, so I was hoping for a standard recommendation on how to protect these pump motors from overcurrent originating from other means (inrush startup, surges, shorts, etc) aside from just inductive kickback. The Operating Instructions manual didn't have quite enough information on this subject to put my mind as ease.