mohpower; I believe the description given to you by SOLA is spot on accurate. There is no question their power conditioners work and work well.
I don't recall ever seeing anything but a sine-wave on the 40 or so that have gone thru my clutches.. We shipped them with a product we sold for many years.
I will say that if you look at all their data sheets you will see over and over, even twice in the same data sheet:
[green]"Output Harmonic Distortion 3% total RMS content at full load"[/green]
Which sounds pretty good to me... BUT! You could read between the lines that this is
only at
full load. At less than full load perhaps you could expect something else...
I can also see that they declare:
[green]"Efficiency up to 92% at full load."[/green]
Boy if that isn't a hedged bet..
"up to" always a giant flag. Plus dependant on a specific condition.
I would still question using one since they really are inefficient at lower ratings. I did mean fry eggs. They will burn the hell out of you. That exposed transformer core probably hits about 200F in normal operation.
I would probably seek another method unless I was running a specific application that essentially ran the Sola at full power all the time.
Keith Cress
Flamin Systems, Inc.-