Are you taking a 1 foot section of the footing? Because I wouldn't assume it would be equivalent to an active earth pressure load, I would assume it would be more of a point load.
Also, another thing I would add is this point load would be spread across a length of a footing, not a one foot section. So your resisting moment should be weight of concrete per area times the length of your footing.
So you could say
Resisting Moment = Weight of footing*entire length
So if your footing is 20 feet long, you could say, 6 ft tall * 1 foot wide * 20 FT LONG * 150 lbs/ft cu = 18000 lbs
and also! the weight of your foot 5*1.5*20*150=22500
Then for the Resisting moment = (18k+22.5k) lbs*centroidx, which would be half your footing length so
40.5k*2.5 ft =101,250 ft lbs
Overturning Moment = mass of cow*approximate speed of cow*height of footing
Weight of cow =4600 lbs
mass of cow = 4600lbs/32.2 lbs/s^2=143 lbs m
momentum of cow (lets say 15 mph to 22 ft per second) = 143 lbs m * 22 ft/s = 3146 lbs F
Give it, a safety factor for time purposes say 5,
3146*5=15730 lbs F
multiply by entire height of wall so, 15730*6 = 94380 ft lbs
So resisting = 101250 ft-lbs
and overturning = 94380 ft-lbs
which resisting>overturning with a safety factor of 5.
I think impact loads should be a concentrated load.
Unless you have a stampede of cows... then you have a serious issue. =)