Soft starter cable sizing thump rule 2

Status
Not open for further replies.

Alms88

Electrical
Joined
Oct 16, 2020
Messages
27
Location
LK
What is the simple thump rule to calculate cable size for DOL starter and soft starters

Motor is 315Kw, 568 FLA, LRa= 3000amps

Soft starter will be voltage ramp from 65% to 100%
10 seconds

Thanks
 
125% of motor full load running current.
Or the appropriate table in the NEC where the ampacity is dictated by motor HP.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
thank you very much
 
There is no change in cable sizing rules based on using a soft starter or any other form of reduced voltage start method.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 