Oct 18, 2020 #1 Alms88 Electrical Joined Oct 16, 2020 Messages 27 Location LK What is the simple thump rule to calculate cable size for DOL starter and soft starters Motor is 315Kw, 568 FLA, LRa= 3000amps Soft starter will be voltage ramp from 65% to 100% 10 seconds Thanks
What is the simple thump rule to calculate cable size for DOL starter and soft starters Motor is 315Kw, 568 FLA, LRa= 3000amps Soft starter will be voltage ramp from 65% to 100% 10 seconds Thanks
Oct 18, 2020 1 Moderator #2 waross Electrical Joined Jan 7, 2006 Messages 28,762 Location CA 125% of motor full load running current. Or the appropriate table in the NEC where the ampacity is dictated by motor HP. Bill -------------------- "Why not the best?" Jimmy Carter Upvote 0 Downvote
125% of motor full load running current. Or the appropriate table in the NEC where the ampacity is dictated by motor HP. Bill -------------------- "Why not the best?" Jimmy Carter
Oct 18, 2020 Thread starter #3 Alms88 Electrical Joined Oct 16, 2020 Messages 27 Location LK thank you very much Upvote 0 Downvote
Oct 19, 2020 1 #4 jraef Electrical Joined May 29, 2002 Messages 11,368 Location US There is no change in cable sizing rules based on using a soft starter or any other form of reduced voltage start method. " We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden Upvote 0 Downvote
There is no change in cable sizing rules based on using a soft starter or any other form of reduced voltage start method. " We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
Oct 19, 2020 Thread starter #5 Alms88 Electrical Joined Oct 16, 2020 Messages 27 Location LK Thank you Upvote 0 Downvote