We are designing a new 70' tall building adjacent to an existing 2-story house. The edge of our new building is about 4' from the existing home (physical gap between the buildings), and nearly 50' higher than the eave height, so it is well within the requirements of ASCE 7-16 section 7.7.2 requiring snow drift on the adjacent structure.
The slope of the existing home's gable roof is approximately 12/12. In the previous section 7.6 regarding unbalanced loading, the unbalanced loads do not need to be accounted for gable roofs with a slope exceeding 7 on 12. Within the commentary of section 7.6, the second paragraph talks about this upper limit "is intended to exclude high-slope roofs on which significant unbalanced loads have not been observed" followed by "the upper bound for the angle of repose of drifted snow is about 30 degrees."
So my question is, is it reasonable to use that same upper limit on the unbalanced snow load on the snow drift calculation. I feel any snow blowing off the upper roof would be subject to the same "sliding" action that the unbalanced snow would be subject to, and fall between the gap between the existing and new building. And if that does make sense, is there any documentation I could present to a code reviewer other than saying my "engineering judgement based on the unbalanced snow load exception" as I know most reviewers would say this doesn't apply, even if it is sound engineering.
Any thoughts/help would be appreciated.