SMRF detailing in low seismic zones

Status
Not open for further replies.

prsconsultant

Structural
Joined
Oct 7, 2003
Messages
152
Location
IN
One of the building we are designing is located in a low seismic zone, but because of poor soil type and building occupancy type IBC 2000 requires us to use a Special Moment Resisting Frame System. My understanding is that irrespective of the seismicity level since we are using a Response Modification Value 'R' of an SMRF, we have to meet all the seismic detailing requirements per chapter 21 of ACI-318. Is this a correct assumption?
 
The detailing must follow the system used based upon the R selected. So if you detail to a particular system, you must use an R equal to or lower than the R indicated for that system.
 