I've got a site retaining wall that I've designed. It varies in height from 4' tall to about 12' tall. The wall is nearly 200' in length.
I know that I need vertical joints in the wall at 20' or so on center in order to deal with shrinkage of the concrete once it is poured.
I have drawn a detail for detailing how the vertical wall joint is to be built. I am having a beveled piece of wood placed on the inside face and outside face of the wall, inside the form, in order to create a vertical groove in the wall, where we want joints.
I also want to provide smooth dowels across each joint to help prohibit differential movement between each segment of wall.
Looking at ACI224, they reference PCA from 1975, and say that the recommendation for the amount of steel required as a dowel is for 0.015 of the cross sectional area of the concrete. In other words, if I have a 16" thick wall, the area of steel dowel needed by this method would be:
(16" wall thickness) x (12" of wall height) x (0.015) = 2.9 square inches/foot of wall height
Which to me, seems VERY excessive.
I was thinking more along the lines of a 3/4" diameter smooth dowel at 18" o.c. Just by feel, I can't imagine that that amount of dowel steel across the joint wouldn't be enough.
What dowel size and spacing do you guys use across a joint like this?
I know that I need vertical joints in the wall at 20' or so on center in order to deal with shrinkage of the concrete once it is poured.
I have drawn a detail for detailing how the vertical wall joint is to be built. I am having a beveled piece of wood placed on the inside face and outside face of the wall, inside the form, in order to create a vertical groove in the wall, where we want joints.
I also want to provide smooth dowels across each joint to help prohibit differential movement between each segment of wall.
Looking at ACI224, they reference PCA from 1975, and say that the recommendation for the amount of steel required as a dowel is for 0.015 of the cross sectional area of the concrete. In other words, if I have a 16" thick wall, the area of steel dowel needed by this method would be:
(16" wall thickness) x (12" of wall height) x (0.015) = 2.9 square inches/foot of wall height
Which to me, seems VERY excessive.
I was thinking more along the lines of a 3/4" diameter smooth dowel at 18" o.c. Just by feel, I can't imagine that that amount of dowel steel across the joint wouldn't be enough.
What dowel size and spacing do you guys use across a joint like this?