Hi schwarz;
my query is not fully answered.The GENSET is meant to be standby duty, typical 8 hours a day. We normally program A/C to start late or early.
Gensets we have specs like say for 15KVA GENSET- 15KVA continuous and 16.5KVA standby max.rating at 0.8 pf. This model has 19bhp @1500rpm engine.
A typical wording on a continous (or prime) rated set may be
"10% overload allowed for 1 hour out of 10 hours"
Standby sets are expected to run far fewer hours, so the 16.5 KVA is allowed at any time.
Apparently not all manufacturers make a distinction between "Continuous Power" and "Prime Power".
Some manufacturers use the same set with different ratings for standby and prime (or continuous). Some manufacturers add bigger oil sumps and possibly other options (oil coolers, larger fans, larger radiators) for continuous power or prime power sets.
warros- how do do we get this figure '13.5 KW, Minimum.' as 7.5KW and 4KW adds up to 11.5KW.
I added 2 KW for running the A/C, and added an additional 4 KW for the starting demand of the A/C unit.
I use a factor of three for starting an A/C unit.
For more than one A/C I add the KWs of the A/Cs and then add 2 X the largest unit for a starting allowance. I have had good luck with these factors for a number of installations of A/Cs on generators.
I appologise for not being more clear in my original post.
pls also explain -"2nd. Rated at 3 phase when 1 phase was ordered. Undersized by 2/3 or %67"
The customer required a 40 KVA set at 120/240 volts. Single phase alternators are not generally manufactured in this size. Typically a three phase set rated at 60 KVA will be used. The alternator will be reconnected for single phase (the double delta connection is the normal connection). The set will be re-rated to 40 KVA. The engine is now oversized, so the allowable power factor increases to unity.
The salesman knew that 3 phase sets were used for single phase but he didn't know that they must be re-rated. He sold a three phase, 40 KVA set that was rerated to 27 KVA.
I called the salesman and he was ademant that the set was properly sized. I pointed out that the main breaker was too small to allow a 40 KVA load. He referred me to the technical department with an appology for sending the wrong breaker.
The tech department explained the de-rating to me very politely. I asked for an explanation in writing. I took the explanation to my customer who went back to the managment of the vendor.
The set had been shipped from the US to Central America, and exchanging it was not a reasonable option. The vendor was reputable and gave a considerable discount to an already low price. The customer was happy to accept the offer and work with me on a curtailing scheme.
NOTE; schwarz;
From the specs, your set appears to be a single phase alternator. This is common at 15 KVA. Above about 20 KVA, reconnected three phase sets become common. This is more in answer to the suggestion to ask the salesman.
respectfully