In my opinion, it is unworkable to specify a slump at the point of placement when a mix is pumped because the pumping operation itself changes the properties of the mix. The supplier does not have control of the pump operation (usually), not all pumps have the same effects, and means of pump operation contributes to how much the concrete properties change. Unless the placement is very slow, and assuming the pump and all pump hoses are properly primed, the stiffening of the mix between delivery and placement is primarily caused by loss of entrained air during the pumping process, usually by about 2% in my experience. If one tests the air content of the mix at the point of delivery, the amount of air entraining admixture can be increased to compensate for air lost. After adjustment for air, the slump at point of placement will be very close to slump at discharge was before the air adjustment. However, the slump at delivery will also be increased and allowances must be made in the specifications to allow for this, or at least in the inspection.