I need some help sizing a booster pump for a closed-loop chilled water system. 3 sketches are attached. I have a large chiller water plant that has 6 secondary pumps is parallel. The pumps each have a VFD and the program maintains DP settings out in the system.
Originally there were only 2 loads and there were never any problems. A third load was recently added with an extremely long piping run to get to the load. This third load is causing problems on design days. On other typical days when flows are not high, there are no problems. Load #1 is the “driving” force for the secondary pumps. Maintaining the 30 psi setpoint at load #1 provides more than enough pressure at loads #2 and #3. Only 3 of the 6 secondary pumps need to run with VFDs in the 60% range. See first sketch.
The second sketch shows what happens on a design day. Since the piping run to Load #3 is so long, in order to provide 6 psig at DP3, my pressures elsewhere are much higher than setpoint. And to make matters worse, all 6 pumps are needed at 100% VFD to meet the DP at load #3. The total combined flow of all loads is not close to the combined pumping capability at reasonable heads. However, I am at the limit of pump head, so additional pumps in parallel essentially do me no good. It is the large pressure drop to get to Load #3 that is killing me, not the flow.
I would like to put a booster pump in the pipeline serving Load #3, but I am not exactly sure how to size it (sketch 3). I know if will have to meet the design flow of Load #3, and it should be variable speed. I assume the best point of control for this pump would be DP3. Physically, the best place to put this pump would be near the Load #3 location. So essentially half of the piping run would be on the booster pump suction and half on the discharge. The load itself, which consist of a heat exchanger bank, control valve, and circuit setter would also be on the discharge side of the booster pump.
My biggest concern would be that this booster pump not interfere hydronically with the secondary pumps and create issues at Load #1 or load #2. So my thought is to size it just for the additional pressure loss in the long piping run. In other words, on a design day in order to maintain 6 psi at Load #3, Load #1 is seeing 50 psi. That is 20 psi more that its setpoint. If I remove that 20 psi from the secondary pumps, I would need to pick it up with the booster pump. So my initial thought is to size the new booster pump for design flow @ 20 psi head. If I include the actual load #3 itself, 26 psi. That way the booster pump is only helping me overcome the additional friction loss in the long piping run and is not affecting the rest of the system …… I think.
Thoughts?
Thoughts?