We are having a 24m by 2.6"m structural column where we would like to have some refurbishment activities (including cutting/welding etc...) on the column, however we have found a presence of hydrocarbons (H2 and H2S) and we are not certain of the concentrations.
We would like to displace/remove the hydrogen, using Nitrogen is not possible due to the volume required and with only four 10mm holes drilled is not feasible. Adding water from the top might introduce static electricity which might lead to a reaction with hydrogen. Are there any other possibilities to inert the column other than N2 or filling with water?
OP,
Both H2 and H2S are highly flammable and explosive gases. In addition H2S is highly toxic. You need to be extremely careful to take the refurbishment work.
LEL/LFL for both H2S and H2 is 4% in air at room temp.
Limiting Oxygen Concentration (LOC) for H2 is also 4%. H2S has no LOC.
Inerting is a very effective and common method of explosion prevention.
It relies on reducing the concentration of the oxidizer (commonly oxygen in air). Inerting is recommended for mixtures having a very low minimum ignition energy (MIE) such as H2.
Usually, a greater volume of N2 is required than CO2 to reduce the oxygen content.
Your concern for water mixing is genuine. In addition to giving rise to static electricity, you will need to take extra effort to dry the column to prevent corrosion.