Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Size cable for DC

Status
Not open for further replies.

pwrtran

Electrical
Apr 25, 2008
341
Hi all

Any ideas about sizing a cable for DC?

Thanks
 
Replies continue below

Recommended for you

DC amps = AC rms amps in terms of cable heating. This would be conservative, since ac ampacity will actually be slightly less than dc ampacity due to skin effect and higher ac resistance.

In terms of voltage drop, inductance is not an issue with dc, only resistance.

As a practical matter, we sized dc circuits just like ac circuits. Unless you have a lot of it and are trying to economize, that approach should work.

What voltage and current level?

David Castor
 
DC sized almost the same as AC like David said.

But since DC loads are often critical loads operating at 125VDC or 48VDC off a battery, voltage drop may be more of an issue. That breaker trip coil may only draw 4 amps but a #14 awg wire could have too much voltage drop to reliably operate the coil if the breaker is a ways out in the switchyard.

 
dpc
The voltage is 125VDC. I think what you said is a good approach!
Thanks!
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor