Site Class F to D change due to pile foundation?

jamoca67

Geotechnical
Joined
Oct 9, 2015
Messages
3
Location
US
Can a site classified as Site Class F due to liquefaction potential have a Site Class D designation change due to pile foundation support?
 
I think that the site class would remain Class F for a traditional foundation pile. An exception might be the use of a rammed aggregate pier or a stone column where liquefiable soil is responsible for the Class F designation where you might be able to argue that the the rammed aggregate pier or stone column could mitigate the risk of liquefaction.
 
Can a site classified as Site Class F due to liquefaction potential have a Site Class D designation change due to pile foundation support?
No.. For piled foundations on sites with liquefaction risk , you should look the requirements of Standard Section 12.13.8.3. The pile design shall consider the effects of liquefaction and liquefaction induced downdrag .
In case of soil improvement ( grouting, stone column ..) you may urge the site class is upgraded to D as ERICREJOIN stated.

 