In the USA, the NEC permits protecting secondary conductors with the primary overcurrent device for a single-phase transformer with a 2-wire secondary. If one end of the secondary winding is earthed, the earth current will be the same as the phase current, so the primary will see the same current (adjusted by the turns ratio). This won't provide sensitive earth fault protection. If the secondary is not earthed, there will be no earth current.