Should rotor earth protection relay of an alternator 45 MW trip the machine when activated?

SA07

Electrical
Joined
Feb 22, 2018
Messages
383
Location
MU
Hi
Can someone advise us? Thanks
 
We determined within my company that we perform a normal shutdown on a rotor ground fault rather than a “trip.” Our rotor circuit are ungrounded so the first ground fault doesn’t cause a large current to flow, but a ground fault could be indicative of a impending and more severe event, so we take the machine offline in a low stress manner and require an inspection.
 