Dear Experts,
I am working on a feasibility study, which requires me to check the compatibility of an installed PSV with new process data.
This valve is 4"x6" and has an orifice of 4" (12.57 sq.in, out of API standards).
The set pressure is 100 barg.
The discharge flange is connected to a 6" vent pipe, to send the gas 163m away (this is the length of the pipe).
At maximum flow, I find a head loss of 67bar through the vent pipe, so the flow is non-critical.
I find a required orifice of 10sq.in, which is quite close to the installed orifice.
If the flow were critical, the required orifice would be 8sq.in, and the margin would be more comfortable.
My question is:
Is it reasonable to enlarge the vent pipe (ie 8"), without changing the valve, using a 6"x8" reducer?
I think it is not a clean solution but it may reassure the client??
Thanks
Nouanda
I am working on a feasibility study, which requires me to check the compatibility of an installed PSV with new process data.
This valve is 4"x6" and has an orifice of 4" (12.57 sq.in, out of API standards).
The set pressure is 100 barg.
The discharge flange is connected to a 6" vent pipe, to send the gas 163m away (this is the length of the pipe).
At maximum flow, I find a head loss of 67bar through the vent pipe, so the flow is non-critical.
I find a required orifice of 10sq.in, which is quite close to the installed orifice.
If the flow were critical, the required orifice would be 8sq.in, and the margin would be more comfortable.
My question is:
Is it reasonable to enlarge the vent pipe (ie 8"), without changing the valve, using a 6"x8" reducer?
I think it is not a clean solution but it may reassure the client??
Thanks