Mar 15, 2024 #1 Tammy16 Electrical Joined Mar 15, 2024 Messages 2 Location CA How will the float charger monitor battery if its connected on bus? Apologies for a bad doodle here.
Mar 16, 2024 Moderator #2 waross Electrical Joined Jan 7, 2006 Messages 28,678 Location CA By a combination of voltage and net charging current. -------------------- Ohm's law Not just a good idea; It's the LAW! Upvote 0 Downvote
By a combination of voltage and net charging current. -------------------- Ohm's law Not just a good idea; It's the LAW!
Mar 16, 2024 #3 crshears Electrical Joined Mar 23, 2013 Messages 1,899 Location CA What Bill said. Welcome! CR "As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV] Upvote 0 Downvote
What Bill said. Welcome! CR "As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
Mar 18, 2024 #4 System Protection Electrical Joined Apr 13, 2023 Messages 87 Location US Are you wondering if the charger can detect if the battery is no longer in the circuit? Upvote 0 Downvote
Mar 18, 2024 Thread starter #5 Tammy16 Electrical Joined Mar 15, 2024 Messages 2 Location CA @System protection Yes, pretty much. We are using eliminator/paralleling circuits and i have no clue how this will work? Upvote 0 Downvote
@System protection Yes, pretty much. We are using eliminator/paralleling circuits and i have no clue how this will work?
Mar 18, 2024 #6 System Protection Electrical Joined Apr 13, 2023 Messages 87 Location US There are current probes that can be installed in series with the battery to detect charging current. Also, some chargers will temporarily drop the float voltage below the battery voltage to ensure the battery is still in the circuit. Kind of a hot topic these days due to TPL-001-5. https://eepowersolutions.com/resour...stem-compliance-with-nerc-standard-tpl-001-5/ https://www.multitel.com/how-to-con...on-non-redundant-station-dc-supply-tpl-001-5/ Upvote 0 Downvote
There are current probes that can be installed in series with the battery to detect charging current. Also, some chargers will temporarily drop the float voltage below the battery voltage to ensure the battery is still in the circuit. Kind of a hot topic these days due to TPL-001-5. https://eepowersolutions.com/resour...stem-compliance-with-nerc-standard-tpl-001-5/ https://www.multitel.com/how-to-con...on-non-redundant-station-dc-supply-tpl-001-5/