sunny81

Electrical
Mar 3, 2010
5
Are the compressive forces acting on a 3 phase bus brace always less than the tensile forces? I say yes, but I am having a hard time to explain this to someone. Am I missing anything? This is my explanation – sum of current in three phases should be zero at any point of time. So, higher currents cannot flow in the same direction and induce a high compressive force.
Is there a way to calculate by what percent these force are lower?
Or am I just dumb and thinking in the wrong direction.
PLease help me understand better.
 
Replies continue below

Recommended for you

Zero-sequence currents all flow in the same direction at the same time.
 
Is this true for a balanced 3 phase system?
 
The forces on bus act to separate the phases. This is true for 3Ø and Ø-Ø faults. There are no forces between phases for 1Ø faults because there is current in only one phase. There may be zero-sequence current in all phases, but except in the faulted phase, the positive- and negative-sequence currents are such that the total current is zero.

Whether this causes compression or tension or cantilever in the braces depends on the geometry of the braces.
 
If there is a grounding transformer on the "load" side of the bus and a ground fault on the "system" side of the bus you can easily have the same zero sequence current in all three phases.
 
You would definitely have the same zero-sequence current in all three phases. This is inherent in the definition of zero-sequence current.
 