Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Shoring Design in Glacial Till

Status
Not open for further replies.

abah2012

Geotechnical
Jan 25, 2012
2
I would appreciate a reference which can guide me for the design of above. The glacial till materials are dense and are to be excavated to a depth of 3 m. The local practice uses soil anchors and shotcrete. I would also appreciate if you tell me other shoring methods.
 
Replies continue below

Recommended for you

A 3m cut can be handled by a cantilever soldier beam or cantilever sheetpile. Anchors are needed for cuts over 4.5 m generally. If you are more than 1.5H (4.5 m) away from any surcharges, you could have a vertical cut in the lower 1.5 m and slope away the upper 1.5 m at 1.5H:1V.
 
I guess the soldier beam is a I beam or a pipe pile.(?) I am in favour of pile pipes. Wonder if the common practice is to drive the cantilever into the soil 7.5 m and then excavate the top 3 m.Or should I have a borehole and then put the pipes and make concrete around it.

What design methods I should use to include the trafic load from the nearby road, etc. Thank you.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor