I have a load bearing masonry building where I planned to transfer diaphragm shears through the joist seats. Problem is that my loads are greater than the rollover capacity as recommended by vulcraft in their "Designing with Vulcraft" book. I'm curious if there are any references where providing masonry infill between joist seats has been used successfully (4-5" of infill based on 4-5" seat). Intuitively it makes sense that it would work, in that the joist seat would transfer load to the CMU infill. But, I'd like there to be some published study and/or research to reference.
Also, I'm totally fine with using misc. steel such as a channel or tube to weld to the deck edge angle and then connect it to the top of the masonry. My only issue with that is that since the joist seats are sloped, I'm concerned about fit-up in the field. IE, the joist seats differ from what I specify and my misc. steel doesn't fit.
Any thoughts?
Thank you!
PS - I saw a similar thread I would have responded to but it was closed
Also, I'm totally fine with using misc. steel such as a channel or tube to weld to the deck edge angle and then connect it to the top of the masonry. My only issue with that is that since the joist seats are sloped, I'm concerned about fit-up in the field. IE, the joist seats differ from what I specify and my misc. steel doesn't fit.