Not sure why you are asking such a basic question, but anyway, here you go:
Section 38.31 of the "ten standards standards"
Horizontal and Vertical Separation
Sewers shall be laid at least 10 feet (3.0 m) horizontally from any existing or proposed water main. The distance shall be measured edge to edge. For gravity sewer where it is not practical to maintain a 10-foot separation, the appropriate reviewing agency may allow deviation of a case-by-case basis, if supported by data from the design engineer. Such deviation may allow installation of the gravity sewer closer to a water main, provided that the water main is in separate trench or on an undisturbed earth shelf located on one side of the sewer and at an elevation so the bottom of the water main is at least 18 inches (46 cm) above the top of the sewer.
If it is impossible to obtain proper horizontal and vertical separation as described above for gravity sewers, both the water main and gravity sewer must be constructed of slip-on or mechanical joint pipe complying with public water supply design standards of the agency and be pressure tested to 150 psi to assure watertightness.
Crossings
Sewers crossing water mains shall be laid to provide a minimum vertical distance of 18inches (46 cm) between the outside of the water main and the outside of the sewer. This shall be the case where the water main is above or below the sewer. The crossing shall be arranged so that the sewer joints will be equidistant and as far as possible from the water main joints. Where a water main crosses under a sewer, adequate structural support shall be provided for the sewer to maintain line and grade.
When it is impossible to obtain proper horizontal and vertical separation as stipulated above, one of the following methods must be specified:
a. The sewer shall be designed and constructed equal to water pipe, and shall be pressure tested at 150 psi. to assure watertightness.
b. Either the water main or the sewer line may be encased in a watertight carrier pipe which extends 10 feet on both sides of the crossing, measured perpendicular to the water main. The carrier pipe shall be of materials approved by the regulatory agency for use in water main construction.