trat1208
Electrical
- Jan 22, 2009
- 15
Hello,
Are there any good relay guys out there that can help me out with the following? I am trying to figure out how tap settings are determined for a KD-10 relay at a MTA other than nameplate. I know how to come up with settings at nameplete MTA using the formula ST/(1+-M).
So for a KD-10 with 75deg nameplate MTA where I need a specific reach at a 90deg MTA instead, I know that adjustments can be made to change the MTA and then the 90deg reach should relate to the ST/(1+-M) tap formula by some factor. How is this correction factor determined?
According to the manual (IL-41.490),
Z_setting = Z_desired at new MTA / (cos (MTA_nameplate - MTA_desired))
However, all of the examples given in the manual are for cases where the desired MTA is less than the nameplate MTA and I am not certain than this formula works for the example I have where I want a 90deg MTA on a 75deg relay.
I am not trying to set a relay, rather I am just trying to decipher some settings that I have on file for one of my stations. The settings I have show taps of T=5.8, S=2, and MTA=-0.03 for both PH-PH and 3PH elements on a KD-10 relay. This equates to 11.96 ohms at nameplate 75deg MTA. The settings say that this gives a desired reach of 12.38 ohm @ 90deg MTA. All of these values that I am talking about are secondary / relay values of course. Unless I am using the above formula wrong, I don't see how it gives me the correction factor that I am looking for.
Do these settings make sense? What math can be done to yield the correction factor that takes me from 11.96 @ 75deg to 12.38 @ 90deg?
Thanks
Are there any good relay guys out there that can help me out with the following? I am trying to figure out how tap settings are determined for a KD-10 relay at a MTA other than nameplate. I know how to come up with settings at nameplete MTA using the formula ST/(1+-M).
So for a KD-10 with 75deg nameplate MTA where I need a specific reach at a 90deg MTA instead, I know that adjustments can be made to change the MTA and then the 90deg reach should relate to the ST/(1+-M) tap formula by some factor. How is this correction factor determined?
According to the manual (IL-41.490),
Z_setting = Z_desired at new MTA / (cos (MTA_nameplate - MTA_desired))
However, all of the examples given in the manual are for cases where the desired MTA is less than the nameplate MTA and I am not certain than this formula works for the example I have where I want a 90deg MTA on a 75deg relay.
I am not trying to set a relay, rather I am just trying to decipher some settings that I have on file for one of my stations. The settings I have show taps of T=5.8, S=2, and MTA=-0.03 for both PH-PH and 3PH elements on a KD-10 relay. This equates to 11.96 ohms at nameplate 75deg MTA. The settings say that this gives a desired reach of 12.38 ohm @ 90deg MTA. All of these values that I am talking about are secondary / relay values of course. Unless I am using the above formula wrong, I don't see how it gives me the correction factor that I am looking for.
Do these settings make sense? What math can be done to yield the correction factor that takes me from 11.96 @ 75deg to 12.38 @ 90deg?
Thanks