I am working on hydraulic oil system for life boat winch operations. The hydrulic oil unit will be operted once in a year for 2-3 hours for testing purposes otherwise it will remain closed until unles in emergency to lift the boat at the platform from sea.
The maximum operating pressure will be 210barg which is needed only once in four year for system certification purpose only.The available piping has design pressure (MAWP) is 220 barg. The piping code is ASME B 31.3 which allows to have accumulation of 20% over pressure for 50 hours at once and 500 hrs per year.
I have two options,
1)I am considering to put the PSV at 230 barg. With 10 % accumulation of PSV the maximum relieving pressure will go upto 253 barg which is 15% over pressure accumulation.
2) Set the PSV set point at 220 barg but this will make set point of PSV very close to max operating pressure and it may cause leakage.
I was wondering that is it safe design. But keeping in view the only once a year for short period of time first option is better.
Need suggestions.
The maximum operating pressure will be 210barg which is needed only once in four year for system certification purpose only.The available piping has design pressure (MAWP) is 220 barg. The piping code is ASME B 31.3 which allows to have accumulation of 20% over pressure for 50 hours at once and 500 hrs per year.
I have two options,
1)I am considering to put the PSV at 230 barg. With 10 % accumulation of PSV the maximum relieving pressure will go upto 253 barg which is 15% over pressure accumulation.
2) Set the PSV set point at 220 barg but this will make set point of PSV very close to max operating pressure and it may cause leakage.
I was wondering that is it safe design. But keeping in view the only once a year for short period of time first option is better.
Need suggestions.