Sequence impedances of a power cable 1

Status
Not open for further replies.

grounded7

Electrical
Jan 10, 2011
11
Hi all,

I am using a network distribution software and trying to create some new cables. For the creation of a cable, I have been given a number of parameters that I need to fill in.

I have a choice; either I can give the radius and GMR of the cable to calculate the positive and zero sequence impedances of the cable or I can simply put in the values of the positive and zero sequence impedances.

I do not have the data to get the software to calculate my impedances. However in the manufacturer data, I have been given the values for: Max AC resistance and reactance. I am using a waveform 4 core cable.

The problem is that I have no idea if this is positive or zero sequence impedance or if its phase impedance.

Can anyone kindly help me out with it?
 
Replies continue below

Recommended for you

It would be the impedance of one cable. When three cables are used for a three phase circuit, that would also be the positive sequence impedance.
 
The positive-sequence impedance, if direct buried or in PVC conduit, would be the table AC resistance and reactance. The manufacturer might be able to give some values for zero-sequence impedance or positive-sequence impedance if installed in metal conduit.
 
Thanks guys. The cables will be laid in ducts, but from what you are saying I can take that:

Positive-seq Z = AC resistance and reactance in the datasheet
Zero-seq = unknown but could be found from the cable manufacturer.

This leads to another question. How essential is it to have the zero-sequence impedance if you are planning to run load-flow and fault analysis on your network?
 
Impossible to get a good ground fault value without the zero-sequence impedance. Load flow doesn't ever use zero-sequence impedance. If you are running a high impedance grounded system you probably don't need the zero-sequence impedance as the fault current will be determined by the grounding resistor, not the cable impedance.
 