I am currently designing a 4-story wood-frame condo bldg. on a post-tension slab above a ground-level garage.

I am accustomed to determining Cs per ASCE7-02 9.5.5.2.1. A maximum, a minimum and also a value between the max and min are determined for Cs.

My question is: My reading of the text implies the minimum value of Cs may be used in determining V, the seismic base shear.

Is this a correct reading?Is there a min Cs of 0.01 in later editions of ASCE7?
Thanks,
Dave in Denver
 
Replies continue below

Recommended for you


The section just sets and upper and lower bound for Cs. You calculate it using Cs = SDS/(R/I) (Eq 9.5.5.2.1-1).

If that value is greater than SD1/T*(R/I) (Eq 9.5.5.2.1-2), you use the value for SD1/T*(R/I). If SDS/(R/I) is smaller than 0.044*SDS*I (Eq 9.5.5.2.1-3), you use the value of 0.044*SDS*I.

If the value of SDS/(R/I) falls between those bounds, then you use that value for design.
 